Am using Klein tools ET600 to check if there is any hidden short to ground (like nail touching any conductor) in any of the 8-conductors in a 60 feet HVAC cable running from indoor air-handler to outdoor heat-pump. I completely disconnect all 8 conductors of HVAC cable from both AirHandler and HeatPump.
Then, I go to Heat Pump outside and connect MegOhmMeter’s Black probe to exposed copper-end of one of the 8 conductors (say the Green conductor). Then connect the MegOhmMeter‘s Red probe to the bare metal copper of the liquid line (as substitute for Ground). Set MegOhMeter dial to 250V. Press “Continuous Lock” followed by pressing “Test”. Display shows 4000 MOhms. Then, if I manually touch the copper end of any of the other conductors (say Orange conductor), display immediately dips down – to say 21 – and rises back up to 4000 MOhms within 2 to 5 seconds. The second time I touch the same conductor (after a minute or so), the dip is not so low – say it might dip to 250 before rising to 4000 MOhms. The third time (again after a minute or so), the dip is a little higher – say to 1000 before rising to 4000 MOhms. By the time I touch it 4th or 5th time, there is NO dip in reading – it stays at 4000 Mohms.
If the Green conductor and Orange conductor (in the above example) do not touch each other electrically, why does resistance value dip and raise? Is there any capacitance build-up in the insulation sheathing? Or should I worry about a short to ground? Is there any current leakage?